Thermostat replacement

daverave

Senior Member
Joined
Nov 29, 2015
Messages
233
Location
Sacramento, CA
We were down in NM in March and wow it’s cold there! Anyway when it’s in the low teens at night we don’t like how often the heater goes on and off so we’d like to replace the FWC Emerson thermostat with one that has a set point lower than 45*. There is a Honeywell “garage” model that can be set at 35* which would be an improvement.
The original thermostat wires are large gauge and were quite difficult to get on the much smaller Honeywell terminals. I’m not sure why they were that gauge… maybe because of the 12 volt power?
Plus the wiring for the original includes a smaller gauge connection that the new one doesn’t have.
See photos in next post for the original and new thermostat wiring. Before I burn down our camper, any opinions on whether this is going to work?
 
daverave said:
We were down in NM in March and wow it’s cold there! Anyway when it’s in the low teens at night we don’t like how often the heater goes on and off so we’d like to replace the FWC Emerson thermostat with one that has a set point lower than 45*. There is a Honeywell “garage” model that can be set at 35* which would be an improvement.
The original thermostat wires are large gauge and were quite difficult to get on the much smaller Honeywell terminals. I’m not sure why they were that gauge… maybe because of the 12 volt power?
Plus the wiring for the original includes a smaller gauge connection that the new one doesn’t have.
See photos in next post for the original and new thermostat wiring. Before I burn down our camper, any opinions on whether this is going to work?
IMG_1225.JPG
 
Note that the original thermostat wiring had the white wire going to the “RC” terminal while the new one is on the “R” terminal.
 
Hmmm... I did the same thing, probably the same thermostat. But I don't recall any issues with the wire gauge. It's nice being able to set the temperature above freezing, but not have it on all night.
 
Note also that the new thermostat is old-school manual while the FWC original is digital. I'm unsure whether that explains the differences in the wiring.
 
Well, no issues here, doing virtually the same thing. Also, it's pretty great being able to set the thermostat above freezing, but not coming on all the time. I kinda think this should be standard; folks (like me) who are unaware of these garage thermostats are suffering with frozen pipes or with a furnace that goes on all the time.
 
I replaced our original thermostat several years ago with a Honeywell manual garage thermostat having a low temp setting of 35 Deg F and which can be mounted horizontally making it easy to access the lever to turn it off and on from the over cab bed. :)

Works perfect.
 
Page 2 of the manual for the CT50K 1028 says:

"For CT50/CT53/CT54: If your old thermostat has 3 or more wires (not counting terminals C or C1), you may have purchased the wrong replacement thermostat. Stop now and call 1-800-468-1502 for advice."

I don't think that red jumper would be considered a third wire but I'd call the number and ask whether it's needed on the CT50K for your furnace.

Link to the User Manual (at the bottom of an Amazon listing for a CT50K)
 
Thanks for everyone's input. It worked just fine, so far. :oops:
Now we're off for several days to explore central Nevada where the furnace and thermostat should get a decent work out.
Dave
 
Hi campers, I found this old thread and am hoping to resurrect it for some answers. I plan to replace the factory analog thermostat on my 2022 FWC Hawk with a Honeywell CT 50 K 1028 thermostat (also analog) in order to have lower temperature settings on the thermostat.
The CT 50 manual says it's for 24 volt ac systems. The FWC is a 12 volt dc system, right? Am I okay using this thermostat on the 12 volt dc FWC?

The CT 50 has a heat anticipator (beneath the faceplate) that can be adjusted to different settings depending on heating system used. The two closest choices in manual seem to be "Warm Air - High Efficiency" with a setting of 0.8, or "Warm Air - Standard" with a setting of 0.4. Anybody know which setting to use?

For OP, your old thermostat had that little red jumper wire as seen in your photo. What did you do with that wire on your new CT 50 ?
 

Try RV LIFE Pro Free for 7 Days

  • New Ad-Free experience on this RV LIFE Community.
  • Plan the best RV Safe travel with RV LIFE Trip Wizard.
  • Navigate with our RV Safe GPS mobile app.
  • and much more...
Try RV LIFE Pro Today
Back
Top Bottom