It seems that I have made an error in my solar panel/controller panel connections but I am not seeing it.
Here is my installed configuration:
I have installed the MPPT 75/15 with a VE.direct dongle. I have also installed a BVM-702 with Temp sensor and VE.direct dongle.
My solar panels (two 100 Watt 18.9V 5.49 A panels connected in parallel) are connected to the PV in terminals of the [SIZE=12pt]The MPPT 75/15 controller[/SIZE][SIZE=12pt]. [/SIZE]
I checked the polarity at the terminal block (see attached picture) that is between the panels and my MPPT 75/15 and I believe the polarity is correct (I used red wires for + and black wires for -)
The red wire from the terminal block is connected to the MPPT 75/15 PV + and the black wire is connected to the MPPT 75/15 -.
The neg pole of my battery is connected to the "battery only" side of the shunt that came with the BVM-702. MPPT Batt - is connected to the other post of the shunt.
The MPPT Batt + is connected through a manual reset 40A circuit breaker and a BlueSea battery selector to the positive terminal of my battery (yes I am aware of the discussion around if this is needed or not but I don't think it is the root of the problem).
My battery comprises two 6V Deep Cycle AGM 200 Ah batteries connected in series for a 12 V, 220 Ah battery bank.
The shunt is also connected to the BVM-702 display using the cable supplied with the display.
The camper load from the IOTA distribution panel is connected to the battery + and - posts (the camper already had an FWC installed IOTA DLS-30 30 Amp , 12 v Power Converter/Charge Controller along with an IOTA DLS-IDP-30 30 Amp AC/DC Distribution/Fuse panel - to which the camper loads are connected e.g. refrigerator, lights, etc).
The system from the battery to the camper load was working just fine before the addition of the solar charger and panels so I do not think there is any issue on that side of the circuit.
The temp sensor is connected to the shunt and appears to be connected correctly as I am able to see the temp on the VE connect display on my iphone.
Problems:
Using the VE connect ap only volts are displayed for the MPPT 75/15 (both watts and amps are zero) and only volts and temperature are displayed for the BVM-702 amps are zero).
The LEDs on the MPPT are both on. The blue LEDs on both dongles are blinking. The BVM-702 display shows volts and temperature but 0 for amps
By the way I did turn on lights and fans but saw no current draw in the VE.Connect display screens only voltages.
This should be easy but I am not seeing the problem.
Request/Question:
I would appreciate it if you would look at the attached images and advise any problems you see.
Regards,